Natural Gas - Pipe Sizing Calculator
Calculate capacities and dimensions of natural gas pipe lines.
The capacity of a low pressure natural gas (less than 1 psi, 6.9 kPa) pipe line with a small pressure loss can be calculated with the Spitzglass formula
q = 3550 k ( h / (l SG))1/2         (1)
q = natural gas volume flow (cfh)
h = pressure drop (in Water Column)
l = length of pipe (ft)
k = [d5 / (1 + 3.6 / d + 0.03 d)]1/2
d = inside diameter pipe (in)
SG = specific gravity of natural gas
For natural gas the nominal BTU/cf varies from about 900 to 1100 BTU/cf. In general it is common to set
  • 1 Cubic Foot (CF) = approx 1000 BTUs
  • 1 CFH = 1 MBH
The specific gravity of natural gas varies from 0.55 to 1.0. Typical values are in the range 0.6 - 0.7.
The downstream pressure in a houseline after the meter/regulator is in general in the range of 7 to 11 inches Water Column, or about 1/4 psi.
Example - Natural Gas Pipe Capacity
The capacity of a 100 ft natural gas pipe with a nominal diameter 0.5 inches (actual ID 0.622 in) and 0.5 inches WC pressure drop can be calculated as
k = [((0.622 in))5/(1 + 3.6 / (0.622 in) + 0.03 (0.622 in))]1/2
= 0.117
q = 3550 0.117 ((0.5 in) / ((100 ft) 0.60) )1/2
= 37.9 (cfh)
Specific gravity of natural gas is set to 0.60.
Natural Gas Pipe Calculator - Imperial Units
Natural Gas Pipe Calculator - Metric Units
  • The Engineering ToolBox (2008). Natural Gas - Pipe Sizing Calculator. [online] Available at: https://www.engineeringtoolbox.com/natural-gas-pipe-calculator-d_1042.html [Accessed Day Month Year].