Three-Phase Power - Equations
Electrical 3-phase equations.
Most AC power today is produced and distributed as three-phase power where three sinusoidal voltages are generated out of phase with each other. With single-phase AC power there is only one single sinusoidal voltage.
Real Power
Line to line voltage:
W applied = 3 1/2 U ll I cos Φ
= 3 1/2 U ll I PF                      (1)
W applied = real power (W, watts)
U ll = line to line voltage (V, volts)
I = current (A, amps)
PF = cos Φ = power factor (0.7 - 0.95)
Line to neutral voltage:
W applied = 3 U ln I cos Φ                    (2)
U ln = line to neutral voltage (V, volts)
For pure resistive load: PF = cos Φ = 1
  • resistive loads converts current into other forms of energy, such as heat
  • inductive loads use magnetic fields like motors, solenoids, and relays
Power Factor
Typical power factors:
Three-Phase Power Factors
DevicePower Factor
Lamp, fluorecent uncompensated 0.5
Lamp, fluorecent compensated 0.93
Lamp, incandescent 1
Motor, induction 100% load 0.85
Motor, induction 50% load 0.73
Motor, induction 0% load 0.17
Motor, synchronous 0.9
Oven, resistive heating element 1
Oven, induction compensated 0.85
Pure resistive load 1
Example - Pure Resistive Load
For pure resistive load and power factor = 1 the real power in a 400/230 voltage (line to line / line to neutral) 20 amps circuit can be calculated as
W applied = 3 1/2 (400 V) (20 A) 1
= 13856 W
= 13.9 kW
Total Power
W = 3 1/2 U I                       (2)
Brake Horsepower
  • Brake horsepower is the actual power delivered to or by a shaft.
W BHP = 3 1/2 U I PF μ / 746                       (3)
W BHP = brake horse power (hp)
μ = device efficiency
  • Electrical